# Can Not Get Float value from Energy Meter using Modbus RTU serial

**URL:** <https://discourse.nodered.org/t/can-not-get-float-value-from-energy-meter-using-modbus-rtu-serial/62921>\
**Category:** General\
**Created:** [22 May 2022 05:20 UTC](https://discourse.nodered.org/t/can-not-get-float-value-from-energy-meter-using-modbus-rtu-serial/62921 "2022-05-22T05:20:16Z")\
**Posts on this page:** 1\
**Showing post:** 12

<div class="post-metadata">

**Author:** ![Steve-Mcl](https://sea2.discourse-cdn.com/flex026/user_avatar/discourse.nodered.org/steve-mcl/32/4826_2.png) [@Steve-Mcl](https://discourse.nodered.org/u/Steve-Mcl)\
**Post date:** [22 May 2022 08:59 UTC](https://discourse.nodered.org/t/can-not-get-float-value-from-energy-meter-using-modbus-rtu-serial/62921/12 "2022-05-22T08:59:05Z")

</div>

As i suspected, addressing is off by 1 - this is a common phenomena in Modbus.

So in which case, take the values from Address 99 & it should work.

From address 99, read 4 values

In buffer parser...

- FloatBE offset 0, length 2, no multiplier
- FloatLE offset 0, length 2, no multiplier

👆 inspect these - 1 set will look right, the other will look wrong.

---