When registering a device, we need to fill 1.register name 2.register address 3.R/W method  
The R/W method has read function 01,02,03,04 write function 05,06,15,16.  
Can i know the details of the list of those R/W method?  
thank you so much

---

<div class="post-metadata">

**Author:** ![Steve-Mcl](https://sea2.discourse-cdn.com/flex026/user_avatar/discourse.nodered.org/steve-mcl/32/4826_2.png) [@Steve-Mcl](https://discourse.nodered.org/u/Steve-Mcl)\
**Post date:** [21 May 2019 21:45 UTC](https://discourse.nodered.org/t/join-device-modbus-device/11372/2 "2019-05-21T21:45:38Z")

</div>

Modbus and it's read write method are well documented. A simple Google search will reveal what these read write functions mean. E.g....

```auto
Function Code	Register Type
1	Read Coil
2	Read Discrete Input
3	Read Holding Registers
4	Read Input Registers
5	Write Single Coil
6	Write Single Holding Register
15	Write Multiple Coils
16	Write Multiple Holding Registers

```

Taken from...  
[https://www.csimn.com/CSI\_pages/Modbus101.html](https://www.csimn.com/CSI_pages/Modbus101.html)