# Node-RED + Modbus RTU over wireless RS-485 bridge – timeout and LoRa duty cycle experience

**URL:** https://discourse.nodered.org/t/node-red-modbus-rtu-over-wireless-rs-485-bridge-timeout-and-lora-duty-cycle-experience/100586
**Category:** General
**Created:** [18 March 2026 05:50 UTC](https://discourse.nodered.org/t/node-red-modbus-rtu-over-wireless-rs-485-bridge-timeout-and-lora-duty-cycle-experience/100586 "2026-03-18T05:50:24Z")
**Posts on this page:** 3
**Page:** 1

<div class="post-metadata">

### Author: ![DafaLin\_NodeRED](https://avatars.discourse-cdn.com/v4/letter/d/a9a28c/32.png) [@DafaLin\_NodeRED](https://discourse.nodered.org/u/DafaLin_NodeRED)
#### Post date: [18 March 2026 05:50 UTC](https://discourse.nodered.org/t/node-red-modbus-rtu-over-wireless-rs-485-bridge-timeout-and-lora-duty-cycle-experience/100586/1 "2026-03-18T05:50:24Z")

</div>

Hi everyone,

I've been using Node-RED to poll Modbus RTU devices over a wireless RS-485 transparent bridge setup. Sharing some notes in case it helps others doing similar industrial IoT work.

**Setup:**

- Node-RED running on a Raspberry Pi
- node-red-contrib-modbus library (Modbus RTU mode)
- RS-485 wireless transparent bridge between Node-RED server and field devices
- RF link: LoRa 920MHz for outdoor runs (~1.5km), WiFi 2.4GHz for indoor
- Field side: 8 Modbus RTU slaves (energy meters, temperature controllers)

**Modbus RTU configuration in Node-RED:**  
Used the Modbus-Flex-Getter node. Key settings:

- Serial port: /dev/ttyUSB0 (connected to wireless bridge master unit)
- Baud rate: 9600, 8-N-1
- Modbus timeout: bumped from default 1000ms to **2000ms** for LoRa link
- Poll interval: 5 seconds per device

**LoRa-specific notes:**  
LoRa 920MHz adds 100-180ms of round-trip latency at default spreading factor (SF7). The wireless bridge handles retransmission internally, so Node-RED just sees a slightly slower serial port.

The key gotcha: LoRa duty cycle. In dense deployments, if you're polling multiple slaves at high rates, you can saturate the RF channel. I found that 5-second poll intervals with 8 devices kept RF utilization comfortable. With faster polling (1s), I saw occasional Modbus CRC errors which were actually from packet collisions on the RF link.

**WiFi mode notes:**  
For the indoor portions, the bridge supports 2.4GHz WiFi transparent mode. Much lower latency (\<20ms), so Modbus timeouts of 500ms work fine. Main issue: WiFi channel congestion in offices -- had to set a fixed channel (ch11 in my case) rather than auto.

**MQTT bridge mode:**  
The bridge also supports a Modbus TCP gateway mode, which lets Node-RED use the Modbus TCP node instead of serial RTU. This worked well for the WiFi link -- set up the bridge as a Modbus TCP slave at 192.168.x.x:502, and Node-RED connects over LAN.

Has anyone else done Modbus RTU over LoRa with Node-RED? Curious what timeout values others use and whether there are other node-red-contrib-modbus settings I should tune.

---

<div class="post-metadata">

### Author: ![DafaLin\_NodeRED](https://avatars.discourse-cdn.com/v4/letter/d/a9a28c/32.png) [@DafaLin\_NodeRED](https://discourse.nodered.org/u/DafaLin_NodeRED)
#### Post date: [29 March 2026 20:09 UTC](https://discourse.nodered.org/t/node-red-modbus-rtu-over-wireless-rs-485-bridge-timeout-and-lora-duty-cycle-experience/100586/2 "2026-03-29T20:09:17Z")

</div>

Quick update after running this for a few more weeks — wanted to share some additional findings in case others are experimenting with similar setups.

**Spreading factor tuning matters more than I expected**

I ended up bumping the LoRa spreading factor from SF7 to SF9 on the longer outdoor runs (~1.2km with partial tree cover). The tradeoff: airtime roughly doubles (about 300-350ms round trip instead of 130-180ms), so I adjusted the Modbus timeout to 3000ms. But link reliability improved significantly — dropped from maybe 2-3% CRC errors down to essentially zero over a 2-week period.

For anyone doing this calculation: at SF9, 868/920MHz with 125kHz bandwidth and a typical 20-byte Modbus RTU frame, you're looking at ~330ms airtime. Stack that with processing and you want at least 2x headroom on the timeout.

**node-red-contrib-modbus reconnect behavior**

One thing I noticed: if the wireless link drops briefly (RF interference, brief obstruction), the Modbus serial node goes into an error state and doesn't always auto-reconnect cleanly. I added a simple error handler that sends a `reconnect` command to the Modbus-Client node after 3 consecutive timeouts. Something like:

```auto
[Modbus-Flex-Getter] --timeout--> [Function: count errors] --if 3x--> [Modbus-Client: reconnect]

```

This made the overall system much more resilient for unattended operation.

**Poll sequencing**

Also switched from parallel polling (inject nodes all firing at 5s intervals independently) to a queued sequential approach using `node-red-contrib-modbus`'s built-in queue mode. This eliminates the scenario where multiple poll requests arrive at the bridge simultaneously and collide on the RF channel. CPU load on the Pi actually went down a bit too.

Hope this is useful for anyone building out similar industrial wireless setups. Happy to share the flow JSON if there's interest.

---

<div class="post-metadata">

### Author: ![system](https://us1.discourse-cdn.com/flex026/uploads/nodered/original/1X/d073cd938eafa2e558d7c2cd59003b3ef4963033.png) [@system](https://discourse.nodered.org/u/system)
#### Post date: [27 June 2026 20:09 UTC](https://discourse.nodered.org/t/node-red-modbus-rtu-over-wireless-rs-485-bridge-timeout-and-lora-duty-cycle-experience/100586/3 "2026-06-27T20:09:45Z")

</div>

This topic was automatically closed 90 days after the last reply. New replies are no longer allowed.