> [@Trying\_to\_learn](#):
>
> I really think you got the NC and NO labels on the High and Low relays the wrong way around.

Yes, I noticed that later, and thought of a better solution.  
What I would do is reverse the float logic by using a resistor between +5v and the float, so that if the float contacts are open, the resistor ensures that the output is +5v.  
However, if the float contacts were closed, it would take the output to 0v.  
I would do it that way because, if the circuit was as it was previously, the 2 input relays would be energised all of the time, and only de-energised when the water level is high, which is not good practice (and a waste of energy).

![float](https://us1.discourse-cdn.com/flex026/uploads/nodered/original/3X/4/e/4e0c8a2299e6c39c06b93279c9e0b56223a9013b.jpeg)

I've not amended the circuit (as I don't know if Bart is interested or not), but well spotted @Trying_to_learn 👍

---

_[View the full topic](https://discourse.nodered.org/t/urgent-electronic-problem-drive-pump-with-2-switches/84221)._