what happens on the receiver side is, that the value is set back to "default" - means that the value is taken again from the temperature sensor itself instead of my "feeding" process
if I send a positive value (e.g. 35) it works perfectly fine
it mentions in the description for that register that it needs to be updated every 30min.
could that be the cause ? based on this i wanted to clarify .. does the negative value ever get written .. but gets replaced by the temp. sensor later on ? (when you write the negative value, did you immediately try to do a read of 33406 to confirm ?)
In your screenshot of the register (at least in the german version of the manual) there seems to be firmware number v20.110 .. did you check if your device is up to date ?
Try contacting Solarfocus technical support because from the modbus communication side of things everything looks ok.
no, the negtaive qty never gets written - it does not change if I send a negative value
and it immediately changes if I send a positive on
after 30 minutes without sending a value is is set back to default and the integrated sensor is sending its data again
the heatpump was installed a few days ago, so my assumption was that I got the latest firmware version