How to solve this problem Roll off Roof observatory
You don't need to look at a new way of doing it, the way we have will work, it may just need a little adjustment. You do need to provide the information required. What is the sequence of inputs? In your earlier posts you had y zero at times so your truth table does not show the full sequence.
If fact if the truth table were sufficient then you could ignore gpioy and say that whenever gpiox is 1 then open the roof and whenever it is 0 then close the roof.
Doesn't that contradict your earlier explanation of :
Maybe it would help us to understand if you showed a complete set of the inputs and outputs you want, e.g.
if X is low and Y is low - then...
if X is low and Y is high - then...
if X is high and Y is low - then...
if X is high and Y is high - then...
and also, if the actions are different when the roof is open, closed, or somewhere in between.
I think this is fairly simple to solve, but the information is incomplete at the moment.
I think I see the problem. On the way from the quiescent state (x and y both 0) to the valid state x and y both 1, it can transiently go through x 1 with y 0 which triggers an undesirable output. The solution is to add a Trigger node between the Join node and the function node, configured like this
That will suppress the transient states and only pass on the final state each time.
All and Colin special
The problem is solved.
I am very happy again thanks. below you see the setup and the final code
When imaging remote stellar object, I use software capture program and LesveDome which is able to control the Observatory. When bad weather / Clouds are there I can automatically close the roof. The weather station is also interacting with the node-red flows
This software is based on the Velleman k8055n. I like to control also all equipment beside to control them with a PC. i use the PI as kind of the heart of the observatory, withn node read installed. I can connect to the observatory via VPN and can connect to node-red dasboard. The roof open en closed is bases on two switchees open and closes which i like to replace with relays. See also in the image.
You understand there must be many fail-proof situations. I must drive two hours before I am there :wink:
Attached the total flow
[{"id":"215a3733.57e8","type":"tab","label":"DeSterrenwacht","disabled":false,"info":""},{"id":"32e3ec6b.89a654","type":"rpi-gpio out","z":"215a3733.57e8","name":"GPIO(12) - Dak Open Pulse","pin":"12","set":true,"level":"0","freq":"","out":"out","x":1380,"y":140,"wires":[]},{"id":"47f3a08.949c4e","type":"trigger","z":"215a3733.57e8","op1":"1","op2":"0","op1type":"num","op2type":"num","duration":"4","extend":false,"units":"s","reset":"","bytopic":"topic","name":"Open Pulse (1 time then send 0)","x":950,"y":140,"wires":[["32e3ec6b.89a654"]]},{"id":"a0b0b2b8.abe5b8","type":"rpi-gpio in","z":"215a3733.57e8","name":"Limit Switch - Roof Closed (24)","pin":"24","intype":"up","debounce":"25","read":true,"x":150,"y":560,"wires":[["c870dd33.c6d758"]]},{"id":"b59df9f7.f90da","type":"rpi-gpio in","z":"215a3733.57e8","name":"Limit Switch - Roof Open (26)","pin":"26","intype":"up","debounce":"25","read":true,"x":140,"y":620,"wires":[["7c2dc368.312894"]]},{"id":"90b3a5a9.0f1f38","type":"rpi-gpio in","z":"215a3733.57e8","name":"Limit Switch - Telescope Parked?","pin":"32","intype":"up","debounce":"25","read":true,"x":150,"y":680,"wires":[["12fbc9b5.ffee6e"]]},{"id":"634de6cd.603f4","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":8,"width":2,"height":1,"name":"Dak Status Limit Switch:","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":730,"y":580,"wires":[],"inputLabels":["2"]},{"id":"c870dd33.c6d758","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 0 : \n    msg.color = \"Green\";\n    msg.payload = \"Dicht\";\n    break;\n    \ncase 2 : \n    msg.color = \"Red\";\n    msg.payload = \"Open\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":440,"y":560,"wires":[["634de6cd.603f4"]]},{"id":"18cc5be.0af1a24","type":"ui_switch","z":"215a3733.57e8","name":"","label":"12V","tooltip":"","group":"4c032911.729c6","order":11,"width":4,"height":1,"passthru":true,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":70,"y":780,"wires":[["29ad7a51.2a269e","315ab6f3.d66c82"]]},{"id":"9e4c6b6a.8c222","type":"ui_switch","z":"215a3733.57e8","name":"","label":"Mount","tooltip":"","group":"4c032911.729c6","order":15,"width":4,"height":1,"passthru":false,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":70,"y":920,"wires":[["3fc6b020.f3f408","9ee84ee5.ca93e"]]},{"id":"83a964d1.0b957","type":"ui_switch","z":"215a3733.57e8","name":"Power PC (220V)","label":"Power PC (220V)","tooltip":"","group":"4c032911.729c6","order":19,"width":4,"height":1,"passthru":true,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":110,"y":1060,"wires":[["6e53b922.8eb64","ef192b37.8aa2e"]]},{"id":"27df4a0a.571f86","type":"ui_switch","z":"215a3733.57e8","name":"","label":"OnFocus","tooltip":"","group":"4c032911.729c6","order":23,"width":4,"height":1,"passthru":true,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":80,"y":1200,"wires":[["3dadb3c0.eac874","bc5311d5.87c3b"]]},{"id":"4ba80116.02e3e","type":"ui_switch","z":"215a3733.57e8","name":"Flat Screen","label":"Flat Screen","tooltip":"","group":"4c032911.729c6","order":31,"width":4,"height":1,"passthru":true,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":90,"y":1320,"wires":[["3a65209c.d37f6","ba5e4716.036008"]]},{"id":"29ad7a51.2a269e","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":340,"y":840,"wires":[["1a11b79a.587048"]]},{"id":"3fc6b020.f3f408","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":340,"y":980,"wires":[["494b5a32.8b9cfc"]]},{"id":"6e53b922.8eb64","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":340,"y":1120,"wires":[["390a6e63.5329ea"]]},{"id":"3dadb3c0.eac874","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":340,"y":1260,"wires":[["56bb4f35.aa4c08"]]},{"id":"3a65209c.d37f6","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":320,"y":1380,"wires":[["6b35652d.109384"]]},{"id":"1a11b79a.587048","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":13,"width":2,"height":1,"name":"12V Status","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":590,"y":840,"wires":[]},{"id":"494b5a32.8b9cfc","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":17,"width":2,"height":1,"name":"Mount Status","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":600,"y":980,"wires":[]},{"id":"390a6e63.5329ea","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":21,"width":2,"height":1,"name":"Power PC (220V)","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":610,"y":1120,"wires":[]},{"id":"56bb4f35.aa4c08","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":25,"width":2,"height":1,"name":"OnFocus","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":580,"y":1260,"wires":[]},{"id":"6b35652d.109384","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":33,"width":2,"height":1,"name":"Flat","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":570,"y":1380,"wires":[]},{"id":"315ab6f3.d66c82","type":"rpi-gpio out","z":"215a3733.57e8","name":"PIN 10","pin":"19","set":true,"level":"0","freq":"","out":"out","x":570,"y":780,"wires":[]},{"id":"9ee84ee5.ca93e","type":"rpi-gpio out","z":"215a3733.57e8","name":"PIN 11","pin":"21","set":true,"level":"0","freq":"","out":"out","x":570,"y":920,"wires":[]},{"id":"ef192b37.8aa2e","type":"rpi-gpio out","z":"215a3733.57e8","name":"PIN 19","pin":"37","set":true,"level":"0","freq":"","out":"out","x":570,"y":1060,"wires":[]},{"id":"bc5311d5.87c3b","type":"rpi-gpio out","z":"215a3733.57e8","name":"","pin":"11","set":true,"level":"0","freq":"","out":"out","x":580,"y":1200,"wires":[]},{"id":"ba5e4716.036008","type":"rpi-gpio out","z":"215a3733.57e8","name":"","pin":"15","set":true,"level":"0","freq":"","out":"out","x":580,"y":1320,"wires":[]},{"id":"22b4b9c9.5f1d36","type":"ui_switch","z":"215a3733.57e8","name":"Canon 40d","label":"Canon 40d","tooltip":"","group":"4c032911.729c6","order":27,"width":4,"height":1,"passthru":true,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":90,"y":1440,"wires":[["9ff84f53.88b03","f92c77e7.779df8"]]},{"id":"df1a9e09.24222","type":"ui_switch","z":"215a3733.57e8","name":"Power Dak","label":"Power Dak","tooltip":"","group":"4c032911.729c6","order":1,"width":4,"height":1,"passthru":true,"decouple":"false","topic":"","style":"","onvalue":"1","onvalueType":"num","onicon":"","oncolor":"","offvalue":"0","offvalueType":"num","officon":"","offcolor":"","x":90,"y":40,"wires":[["bed82094.0ad898","ff016a48.efb328"]]},{"id":"9ff84f53.88b03","type":"rpi-gpio out","z":"215a3733.57e8","name":"","pin":"33","set":true,"level":"0","freq":"","out":"out","x":580,"y":1440,"wires":[]},{"id":"bed82094.0ad898","type":"rpi-gpio out","z":"215a3733.57e8","name":"","pin":"35","set":true,"level":"0","freq":"","out":"out","x":560,"y":40,"wires":[]},{"id":"f92c77e7.779df8","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":320,"y":1500,"wires":[["12573220.9338b6"]]},{"id":"ff016a48.efb328","type":"function","z":"215a3733.57e8","name":"Color Mappings","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Aan\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Uit\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":320,"y":100,"wires":[["37097c2d.45e5bc"]]},{"id":"12573220.9338b6","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":29,"width":2,"height":1,"name":"40d","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":570,"y":1500,"wires":[]},{"id":"37097c2d.45e5bc","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":2,"width":2,"height":1,"name":"","label":"Status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":560,"y":100,"wires":[]},{"id":"12fbc9b5.ffee6e","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 0 : \n    msg.color = \"Green\";\n    msg.payload = \"Parked\";\n    break;\n    \ncase 1 : \n    msg.color = \"Red\";\n    msg.payload = \"Not Parked\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":440,"y":680,"wires":[["a5c22ef4.b2e1c8"]]},{"id":"a5c22ef4.b2e1c8","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":10,"width":4,"height":1,"name":"`Telescope Park","label":"Telescope:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":700,"y":680,"wires":[]},{"id":"7c2dc368.312894","type":"function","z":"215a3733.57e8","name":"Color Mapping","func":"switch (msg.payload) {\n\ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"Open\";\n    break;\n    \ncase 2 : \n    msg.color = \"Green\";\n    msg.payload = \"Open\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":440,"y":620,"wires":[["634de6cd.603f4"]]},{"id":"fb39ba69.591768","type":"wake on lan","z":"215a3733.57e8","mac":"90-B1-1C-A4-1E-BC","host":"","udpport":9,"name":"WakeUp Obs","x":310,"y":1880,"wires":[]},{"id":"def5286.17fa458","type":"ui_button","z":"215a3733.57e8","name":"","group":"4c032911.729c6","order":4,"width":2,"height":1,"passthru":false,"label":"WakeUp PC","tooltip":"","color":"","bgcolor":"","icon":"","payload":"","payloadType":"str","topic":"","x":90,"y":1880,"wires":[["fb39ba69.591768","9eb92ebf.83b5c8"]]},{"id":"8e6ad9f9.da356","type":"ui_button","z":"215a3733.57e8","name":"","group":"4c032911.729c6","order":6,"width":2,"height":1,"passthru":false,"label":"Opening Roof","tooltip":"","color":"","bgcolor":"","icon":"","payload":"","payloadType":"str","topic":"","x":100,"y":140,"wires":[["47f3a08.949c4e"]]},{"id":"5b9d83ab.0b72d4","type":"ui_button","z":"215a3733.57e8","name":"","group":"4c032911.729c6","order":7,"width":2,"height":1,"passthru":false,"label":"Closing Roof","tooltip":"","color":"","bgcolor":"","icon":"","payload":"","payloadType":"str","topic":"","x":90,"y":480,"wires":[["94ffacc9.0e1448"]]},{"id":"fa37b129.456d5","type":"rpi-gpio out","z":"215a3733.57e8","name":"GPIO(38) - Dak Dicht Pulse","pin":"38","set":true,"level":"0","freq":"","out":"out","x":1380,"y":480,"wires":[]},{"id":"94ffacc9.0e1448","type":"trigger","z":"215a3733.57e8","op1":"1","op2":"0","op1type":"str","op2type":"str","duration":"4","extend":false,"units":"s","reset":"","bytopic":"topic","name":"Clossing Pulse (1 time then send 0)","x":940,"y":480,"wires":[["fa37b129.456d5"]]},{"id":"9eb92ebf.83b5c8","type":"trigger","z":"215a3733.57e8","op1":"1","op2":"0","op1type":"str","op2type":"str","duration":"250","extend":false,"units":"ms","reset":"","bytopic":"topic","name":"","x":320,"y":1840,"wires":[["bb095c96.9bb328"]]},{"id":"bb095c96.9bb328","type":"function","z":"215a3733.57e8","name":"delay to start","func":"switch (msg.payload) {\n\ncase 1 : \n    msg.color = \"Green\";\n    msg.payload = \"Wait Starting PC\";\n    break;\n    \ncase 0 : \n    msg.color = \"Red\";\n    msg.payload = \"PC is on\";\n    break;\n    \ndefault : \n    msg.color = \"Gray\";\n    msg.payload = \"not set\";\n    break;\n}\n\nreturn msg;","outputs":1,"noerr":0,"x":510,"y":1840,"wires":[["ef38847b.e1e888"]]},{"id":"ef38847b.e1e888","type":"ui_text","z":"215a3733.57e8","group":"4c032911.729c6","order":39,"width":0,"height":0,"name":"","label":"status:","format":"<font color= {{msg.color}} > {{msg.payload}} </font>","layout":"row-left","x":670,"y":1840,"wires":[]},{"id":"5a8fb482.5e428c","type":"switch","z":"215a3733.57e8","name":"if 1","property":"payload","propertyType":"msg","rules":[{"t":"eq","v":"1","vt":"str"}],"checkall":"true","repair":false,"outputs":1,"x":910,"y":240,"wires":[["47f3a08.949c4e"]]},{"id":"11b4b75b.9722f9","type":"switch","z":"215a3733.57e8","name":"if 1","property":"payload","propertyType":"msg","rules":[{"t":"eq","v":"1","vt":"str"}],"checkall":"true","repair":false,"outputs":1,"x":910,"y":400,"wires":[["94ffacc9.0e1448"]]},{"id":"abecf556.29c568","type":"rpi-gpio in","z":"215a3733.57e8","name":"LesveDome Relay (22)","pin":"22","intype":"down","debounce":"1000","read":true,"x":120,"y":280,"wires":[["f1e936b4.9da938","a672d795.c0be2"]]},{"id":"6afbdacb.ccf154","type":"rpi-gpio in","z":"215a3733.57e8","name":"LesveDome Relay (Close) (13)","pin":"13","intype":"down","debounce":"1000","read":true,"x":140,"y":360,"wires":[["6609ab59.5a88b4","667e3bb5.5ee874"]]},{"id":"6609ab59.5a88b4","type":"debug","z":"215a3733.57e8","name":"gpioy-pin","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":380,"y":400,"wires":[]},{"id":"667e3bb5.5ee874","type":"change","z":"215a3733.57e8","name":"gpioy","rules":[{"t":"set","p":"topic","pt":"msg","to":"gpioy","tot":"str"}],"action":"","property":"","from":"","to":"","reg":false,"x":530,"y":360,"wires":[["ce2e552e.c0598","b417c3c2.655a6"]]},{"id":"b417c3c2.655a6","type":"join","z":"215a3733.57e8","name":"","mode":"custom","build":"object","property":"payload","propertyType":"msg","key":"topic","joiner":"\\n","joinerType":"str","accumulate":true,"timeout":"0","count":"2","reduceRight":false,"reduceExp":"","reduceInit":"","reduceInitType":"","reduceFixup":"","x":690,"y":320,"wires":[["aade8709.62a2d8","902926fe.597468"]]},{"id":"aade8709.62a2d8","type":"debug","z":"215a3733.57e8","name":"Join","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":710,"y":240,"wires":[]},{"id":"185250d.2f8522f","type":"function","z":"215a3733.57e8","name":"If statement","func":"let gpioa = 0\nlet gpiob = 0\n// Open IF\nif (msg.payload.gpiox == 1  && msg.payload.gpioy == 1) {\n    node.send([{payload: 1},{payload: 0}])\n}\n// Close If\nif (msg.payload.gpiox == 0 && msg.payload.gpioy == 1) {\n    node.send([{payload: 0},{payload: 1}])\n}\nreturn      // don't return a message here as have already done it","outputs":2,"noerr":0,"x":1030,"y":320,"wires":[["1a7b8ca1.efe163","5a8fb482.5e428c"],["404f162e.76bdf","11b4b75b.9722f9"]]},{"id":"ce2e552e.c0598","type":"debug","z":"215a3733.57e8","name":"gpioy","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":550,"y":420,"wires":[]},{"id":"a672d795.c0be2","type":"change","z":"215a3733.57e8","name":"gpiox","rules":[{"t":"set","p":"topic","pt":"msg","to":"gpiox","tot":"str"}],"action":"","property":"","from":"","to":"","reg":false,"x":530,"y":280,"wires":[["9ec52014.2de1e","b417c3c2.655a6"]]},{"id":"f1e936b4.9da938","type":"debug","z":"215a3733.57e8","name":"gpiox-pin","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":360,"y":240,"wires":[]},{"id":"9ec52014.2de1e","type":"debug","z":"215a3733.57e8","name":"gpiox","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":530,"y":220,"wires":[]},{"id":"1a7b8ca1.efe163","type":"debug","z":"215a3733.57e8","name":"Open","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":1230,"y":280,"wires":[]},{"id":"404f162e.76bdf","type":"debug","z":"215a3733.57e8","name":"Close","active":false,"tosidebar":true,"console":false,"tostatus":false,"complete":"payload","targetType":"msg","x":1230,"y":340,"wires":[]},{"id":"902926fe.597468","type":"trigger","z":"215a3733.57e8","op1":"Nothing","op2":"","op1type":"str","op2type":"payl","duration":"100","extend":true,"units":"ms","reset":"","bytopic":"all","name":"Supress transients","x":850,"y":320,"wires":[["185250d.2f8522f"]]},{"id":"4c032911.729c6","type":"ui_group","z":"","name":"Schakelaars","tab":"f4f3f5b4.649508","order":1,"disp":true,"width":8,"collapse":true},{"id":"f4f3f5b4.649508","type":"ui_tab","z":"","name":"DeSterrenWacht","icon":"dashboard","disabled":false,"hidden":false}]
anyway everybody thanks, and special colin, and sorry that it was somee time hard to explain i think that was cause also by the the language.
Regards
Chris
I am sure you did a much better job explaining in English than I would have done in your language.
Glad to be of help.
Well done! Clear skies, and good observing :smiley: