I have published the Node-RED flows that heat our house: GitHub - avk999/heating-control: Node-RED boiler (OpenTherm/OTGW) and TRV heating control for Home Assistant · GitHub
What it does. One gas boiler (OpenTherm, through an OpenTherm Gateway) and five battery-powered radiator valves (TRVs), five rooms, each with a virtual thermostat in Home Assistant. Node-RED decides the boiler flow temperature and every TRV setpoint, and exports its internal state to Prometheus for a Grafana dashboard and alerts. It has run since October 2026.
How it works.
- Boiler loop, every 15 s: the room with the largest deficit leads; its error feeds node-red-contrib-pid, and the output is mapped to a 20 to 75 C flow temperature on a convex curve and written as the OpenTherm control setpoint.
- TRV loop: a PI controller per room on the room sensor writes the TRV setpoint. The TRV's own sensor is never used for control.
- When the leading room's mode or target changes, or a room warms by 2 K in 30 min from the sun or a fireplace, the PID integral is corrected by that step through
msg.integral, so the loop does not spend hours unwinding stale history. - Schedules with cron-plus, radar presence and a door contact; dead-sensor detection; an off switch that hands the boiler back to the wall thermostat and opens every valve.
Things measured on the way that may save someone time.
- TRV sensors next to the radiator are off by an amount that swings about 3 K with valve state, so no calibration offset works. Control on a room sensor instead.
- Derivative made things worse: room sensors report in 0.1 K steps and D turned them into command spikes. Lowering the proportional band fixed both the slow start and the overshoot.
- Deduplicate TRV writes against the setpoint the valve reports, not against the last value sent. A valve that silently reverted was left alone for 9.9 h the other way.
- Zero error does not mean zero output. Skipping the PID when no room wanted heat switched the boiler about 300 times a day in simulation.
- A
generic_thermostatstays available when its source sensor dies; setexpire_afteron MQTT sensors. node.error(text)without the msg argument never reaches a Catch node.
The repo has both flows, the dashboard, example HA configuration, the alert rules, a user guide with every tunable, and a document with the measurements behind each decision.
Thanks to @Colin for node-red-contrib-pid, and for reviewing and merging the runtime integral setting (2.1.0) this depends on; to Schelte Bron for the OpenTherm Gateway; to Robert van den Breemen for OTGW-firmware; and to the authors of node-red-contrib-home-assistant-websocket, node-red-contrib-cron-plus and node-red-contrib-prometheus-exporter.
Comments and questions welcome.