Hello everyone,
i´m trying to connect my PLC over the Client with Node-RED.
i added in my Client a Server with the correct address (hopefully
)but i receive this error " Client node error on: error: [" OPC UA connection error: End point must exist opc.tcp://139.6.134.110:4840"]".
when i Change somthing on my PLC changes the value on Client, which means they are connected, but i can't connect my Client with Node-RED.
could someone help me please?

is the node-red server on the same IP address range as the opc server?
Add node-red-node-ping and see if you can ping 139.6.134.110 from node-red.
No. Just feed the ping to a debug node. Do you get successful pings from node-red to the OPC server?
that looks to be connected correctly
i copied my OPC URL from my Client, everythings looks good, but when i use OPCUA-Client in Node-RED i receive the errors
have you entered that full URL into the ping node?
Ping only operates on hostname or IP
Only enter the IP 139.6.134.110 - check again
i get the massage: "some configurations-node are not used, klich hier to see"
when i click i see what in Picture
when i choose one of them, the same thing happens like the last picture
you have multiple unused config nodes - delete the ones not in use.
does ping work?
is OPC now working?
If not, I can only suggest you read through the issues on the projects github issues pages - you might find a solution.