Opentherm Thermostat
Hi guys,
I want to share my implementation of Opentherm Tasmota and its integration with a template node in Node Red Dashboard.
I use it to remotely command the central heating boiler into my holiday house.
The hardware is based on a Wemos D1 ESP8266, with just an Opentherm Shield for levels compensation and a DS18B20 digital temperature sensor.
This is the Dashboard Template i made (with some CSS involved):
  • on the left panel the measured temperature (DS18B20 sensor)
  • at its right, the temperature setpoint
  • at the far right, on top the power button which has three state, off (greyed out), auto (blue), heating on (red) ... this is a clickable / status button
  • at its bottom, the flame status (greyed = off, red = on)
  • under temp set point the two buttons to increase the temp set point or decrease it (clickable buttons with icons)
  • at the very bottom, a string with all the most important datas coming from Opentherm communication with boiler
Here with heating turned off, ambient temperature = 17,3 C and setpoint ad 19,5 C
Heating turned on (auto) but setpoint lower than ambient temperature
Heater turned on but flame not yet on.
Heating turned on and boiler flame on
In the opentherm message status row some informations are displayed, such as:
connection status
Flame modulation
Boiler temperature (measured)
Water temperature (measured)
Central heating status (1 / 0)
Flame status (1 / 0)
Boiler temperature (setpoint)
Water temperature (setpoint)
Water pressure
Fault status
I hope someone enjoy, feel free to ask for more information!
Would you perhaps share you code?
Sure,
here it is.
Screenshot
Code
        "id": "7bd28316dc37d295",
        "type": "tab",
        "label": "Thermo2",
        "disabled": true,
        "info": "",
        "env": []
        "id": "d721b34520a32a61",
        "type": "change",
        "z": "7bd28316dc37d295",
        "name": "temp_set",
        "rules": [
                "t": "set",
                "p": "temp_set",
                "pt": "flow",
                "to": "19.5",
                "tot": "num"
                "t": "set",
                "p": "temp_set",
                "pt": "msg",
                "to": "temp_set",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 300,
        "y": 280,
                "fbd7edfb9e617ee1"
        "id": "fbd7edfb9e617ee1",
        "type": "change",
        "name": "temp_amb",
        "rules": [
                "t": "set",
                "p": "temp_amb",
                "pt": "flow",
                "to": "20.0",
                "tot": "num"
                "t": "set",
                "p": "temp_amb",
                "pt": "msg",
                "to": "temp_amb",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 450,
        "y": 280,
                "5e92c010cbf93331"
        "id": "ae894b52eb94ae0b",
        "type": "ui_template",
        "group": "e15b980fd008f6a8",
        "name": "Thermostat Template",
        "order": 4,
        "width": "6",
        "height": "4",
        "format": "<style>\n    . {\n        box-sizing: border-box;\n        font-family: \"Roboto\",\"Helvetica Neue\", sans-serif ;\n    }\n\n    .container {\n        display: flex;\n        width: 100%;\n        height: 100%;\n        background-color: #303030;\n    }\n\n\n    .centerme {\n        display: flex;\n        text-align: center;\n        justify-content: center;\n        align-items: center;\n        margin: 4px;\n    }\n\n    .roundme {\n        border: 2px solid black;\n        border-radius: 8px;\n        background-color: #222222;\n        box-shadow: inset 2px 2px 3px 4px rgba(0, 0, 0, 0.1);\n        background: rgb(5, 5, 5);\n        background: linear-gradient(135deg, rgba(5, 5, 5, 1) 0%, rgba(42, 42, 42, 1) 100%);\n        margin: 3px;\n    }\n    \n    .roundme2 {\n        border: 2px solid black;\n        border-radius: 8px;\n        background-color: #222222;\n        box-shadow: inset 2px 2px 3px 4px rgba(0, 0, 0, 0.1);\n        background: rgb(5, 5, 5);\n        margin: 3px;\n    }\n\n    .a1 {\n        /*    background-color:red; */\n        height: 25px;\n        margin-bottom: 1px;\n        font-size: 16px;\n        color: #6689A1;\n        padding-bottom: 4px;\n        border-bottom: 2px solid #DD7F00;\n\n    }\n\n    .a2 {\n        /*    background-color:red; */\n        height: 100%;\n        margin-top: 1px;\n        font-size: 60px;\n        color: #D7DBDD;\n\n    }\n\n    .b1 {\n        color: #6689A1;\n        height: 25px;\n        margin-bottom: 1px;\n        font-size: 16px;\n        padding-bottom: 4px;\n        border-bottom: 2px solid #DD7F00;\n    }\n\n    .b2 {\n        height: 100%;\n        margin-top: 1px;  \n        font-size: 28px;\n        color: #D7DBDD;\n    }\n\n    .gradient-2 {\n    background: linear-gradient(135deg, rgba(5, 5, 5, 1) 0%, rgba(42, 42, 42, 1) 100%) padding-box,\n    linear-gradient(to right, #F16F0F, #F43700) border-box;\n    margin-top:14px;\n    border-radius: 20px;\n    border: 6px solid transparent;\n    }\n    \n    .red_color {\n        color: #FF0000;\n    }\n    \n    .grey_color {\n        color: #444444;\n    }\n\n    .blue_color {\n        color: #00DAF4;\n    }\n    \n    \n    .otstatus {\n        padding-left: 6px;\n        padding-top: 2px;\n        font-size: 14px;\n\n    }\n\n@keyframes fire {\n  from {color: #FF5B33;}\n  50% {color: #FFAC33;}\n  to {color: #FF5B33;}\n}\n\n.on_fire {\n  animation-name: fire;\n  animation-duration: 2000ms;\n  animation-iteration-count:infinite;\n}\n\n\n\n</style>\n\n<div class=\"container\" layout=\"column\">\n    <div layout=\"row\" flex=\"80\">\n        <div layout=\"column\" flex=\"50\" class=\"roundme\">\n            <div class=\"a1 centerme\">Temp Ambiente</div>\n            <div class=\"a2 centerme\" ng-class=\"temp_amb_status\" ng-model=\"temp_amb_status\" ng-bind-html=\"temp_amb_ | number: 1\"></div>\n        </div>\n    \n        <div flex=\"50\" layout=\"column\">\n            <div flex=\"70\" layout=\"row\">\n    \n                <div layout=\"column\" flex=\"60\" class=\"roundme\">\n                    <div class=\"b1 centerme\">Temp Set</div>\n                    <div class=\"b2 centerme\"  ng-bind-html=\"temp_set_ | number: 1\" ></div>\n                </div>\n    \n                <div flex=\"40\" layout=\"column\">\n                    <div flex=\"50\" class=\"centerme roundme\" ng-click=\"click_power();\">\n                        <md-icon md-font-icon=\"power_settings_new\" style=\"font-size:32px\" ng-class=\"power_status_icon\"></md-icon>\n                    </div>\n                    <div flex=\"50\" class=\"centerme roundme\">\n                        <md-icon md-font-icon=\"local_fire_department\" style=\"font-size:32px\" ng-class=\"heating_status_icon\"></md-icon>\n                    </div>\n                </div>\n    \n            </div>\n            <div flex=\"30\">\n                <div layout=\"row\" style=\"height:100%\">\n                    <md-button flex=\"50\" class=\"centerme roundme\" ng-click=\"click_temp_minus()\">\n                        <md-icon md-font-icon=\"remove\" style=\"font-size:32px\"></md-icon>\n                    </md-button>\n                    <md-button flex=\"50\" class=\"centerme roundme\"  ng-click=\"click_temp_plus()\">\n                        <md-icon md-font-icon=\"add\" style=\"font-size:32px\"></md-icon>\n                    </md-button>\n                </div>\n            </div>\n        </div>\n    </div>\n\n    <div layout=\"row\" flex=\"20\" class=\"roundme2 otstatus\">\n        <div layout=\"column\">    \n            <div flex=\"50\" ng-bind-html=\"ot_status1\"></div>\n            <div flex=\"50\" ng-bind-html=\"ot_status2\"></div>\n        </div>\n    </div>\n</div>\n\n<script>\n    (function(scope) {\n\n  scope.$watch('msg', function(msg) \n    {\n\n        if(msg.hasOwnProperty('temp_set')) {\n        scope.temp_set_ = msg.temp_set;\n        }\n\n        if(msg.hasOwnProperty('temp_amb')) {\n                scope.temp_amb_ = msg.temp_amb;\n        }\n\n        if(msg.hasOwnProperty('heating')) {\n            if(msg.heating==\"on\") {\n                scope.temp_amb_status=\"gradient-2\";\n            }\n            if(msg.heating==\"off\") {\n                scope.temp_amb_status=\"\";\n            }     \n        }\n    \n        // Opentherm status\n        if(msg.hasOwnProperty('ot_status1')) {\n            scope.ot_status1 = msg.ot_status1;\n            scope.ot_status2 = msg.ot_status2;\n        }\n\n        // Power status check    \n        if(msg.hasOwnProperty('power_status')) {\n            if(msg.power_status==true) {\n                scope.power_status_icon=\"blue_color\";\n            }\n            if(msg.power_status==false) {\n                scope.power_status_icon=\"grey_color\";\n            }     \n        }\n\n        // Heating status check\n        if(msg.hasOwnProperty('heating_status')) {\n            if(msg.heating_status==1) {\n                scope.power_status_icon=\"red_color\";\n            }\n        }\n    \n        // Flame status check\n        if(msg.hasOwnProperty('flame_status')) {\n            if(msg.flame_status==true) {\n//                scope.heating_status_icon=\"red_color\";\n                scope.heating_status_icon=\"on_fire\";\n\n            }\n            if(msg.flame_status==false) {\n                scope.heating_status_icon=\"grey_color\";\n            }\n        }\n        // End flame status check //\n\n        return;\n    });  \n\n    scope.click_power = function() {\n        scope.send({ \"payload\": \"power\"});\n    }\n\n    scope.click_temp_plus = function() {\n        scope.send({ \"payload\": \"temp_plus\"});\n    }\n\n    scope.click_temp_minus = function() {\n        scope.send({ \"payload\": \"temp_minus\"});\n    }\n  \n})(scope);\n\n</script>\n\n",
        "storeOutMessages": false,
        "fwdInMessages": false,
        "resendOnRefresh": false,
        "templateScope": "local",
        "className": "",
        "x": 920,
        "y": 380,
                "da16bc54c2ef5db2"
        "id": "da16bc54c2ef5db2",
        "type": "function",
        "name": "Thermostat logic",
        "func": "var power_status = flow.get('power_status');\nvar temp_set = flow.get('temp_set'); \nvar temp_amb = flow.get('temp_amb');\nvar heating_status = flow.get('heating_status');\nvar ot_status1 =  flow.get('ot_status1');\nvar ot_status2 =  flow.get('ot_status2');\nvar flame_status =  flow.get('flame_status');\nvar ch_status =  flow.get('ch_status');\nvar msg2 = { payload: \"payload\", topic: \"topic\" }\n\nif(msg.hasOwnProperty('ot_status1')){\n    flow.set('ot_status1',msg.ot_status1);\n    flow.set('ot_status2',msg.ot_status2);\n}\n\nif(msg.hasOwnProperty('flame_status')){\n    flow.set('flame_status',msg.flame_status);\n}\n\nif(msg.hasOwnProperty('ch_status')){\n    flow.set('ch_status',msg.ch_status);\n}\n\nif(msg.payload==\"power\"){\n    power_status = !power_status;\n    flow.set('power_status',power_status);\n}\n\nif(msg.payload==\"temp_plus\"){\n    temp_set = temp_set + 0.5;\n    flow.set('temp_set',temp_set);\n}\n\nif(msg.payload==\"temp_minus\"){\n    temp_set = temp_set - 0.5;\n    flow.set('temp_set',temp_set);\n}\n\nif(power_status){\n    if(heating_status)\n    {\n\n        // riscaldamento acceso e temperatura set minore o uguale di temp ambiente\n        if (temp_set <= temp_amb+0.2) {\n            heating_status = false;\n        }\n    }\n    else\n    {\n        // riscaldamento spento e temperatura set maggiore di temp ambiente\n        if (temp_set > temp_amb+0.2) {\n            heating_status = true;\n        }\n\n    } \n\n    flow.set('heating_status', heating_status);\n}\nelse{\n    heating_status = false;\n    flow.set('heating_status', heating_status); \n}\n\nmsg.power_status = flow.get('power_status');\nmsg.temp_amb = flow.get('temp_amb');\nmsg.temp_set = flow.get('temp_set');\nmsg.ot_status1 = flow.get('ot_status1');\nmsg.ot_status2 = flow.get('ot_status2');\nmsg.flame_status = flow.get('flame_status');\nmsg.ch_status = flow.get('ch_status');\nmsg.heating_status = flow.get('heating_status');\n\nif (flow.get('heating_status')) {\n msg2.payload = 1;\n} else {\n msg2.payload = 0;\n}\n\nreturn [msg, msg2];",
        "outputs": 2,
        "noerr": 0,
        "initialize": "",
        "finalize": "",
        "libs": [],
        "x": 910,
        "y": 440,
                "ae894b52eb94ae0b"
                "9733bb3381da8ff6"
        "id": "a9865b0db96580e8",
        "type": "change",
        "rules": [
                "t": "set",
                "p": "payload",
                "pt": "msg",
                "to": "true",
                "tot": "bool"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 660,
        "y": 600,
                "da16bc54c2ef5db2"
        "id": "3293b42b8867bdb3",
        "type": "switch",
        "property": "payload",
        "propertyType": "msg",
        "rules": [
                "t": "eq",
                "v": "connect",
                "vt": "str"
        "checkall": "true",
        "repair": false,
        "outputs": 1,
        "x": 510,
        "y": 600,
                "a9865b0db96580e8"
        "id": "820176597df91726",
        "type": "ui_ui_control",
        "events": "connect",
        "x": 340,
        "y": 600,
                "3293b42b8867bdb3"
        "id": "5c6643565e2ddab2",
        "type": "inject",
        "props": [
                "p": "payload"
                "p": "topic",
                "vt": "str"
        "repeat": "",
        "crontab": "",
        "once": true,
        "onceDelay": "0.2",
        "topic": "",
        "payload": "",
        "payloadType": "date",
        "x": 370,
        "y": 640,
                "3293b42b8867bdb3"
        "id": "5e92c010cbf93331",
        "type": "change",
        "name": "power_status",
        "rules": [
                "t": "set",
                "p": "power_status",
                "pt": "flow",
                "to": "false",
                "tot": "bool"
                "t": "set",
                "pt": "msg",
                "to": "power_status",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 620,
        "y": 280,
                "c98ab4ede699f7b7"
        "id": "c98ab4ede699f7b7",
        "type": "change",
        "name": "heating_status",
        "rules": [
                "t": "set",
                "p": "heating_status",
                "pt": "flow",
                "to": "false",
                "tot": "bool"
                "t": "set",
                "pt": "msg",
                "to": "heating_status",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 180,
        "y": 340,
                "60021c373e8cdb53"
        "id": "5cb475e23794806d",
        "type": "inject",
        "props": [
                "p": "payload"
        "repeat": "",
        "crontab": "",
        "once": true,
        "onceDelay": 0.1,
        "topic": "",
        "payload": "true",
        "payloadType": "bool",
        "x": 150,
        "y": 280,
                "d721b34520a32a61"
        "id": "5c63f60ed55988e0",
        "type": "mqtt in",
        "topic": "tele/thermostat/SENSOR",
        "qos": "1",
        "datatype": "auto-detect",
        "broker": "51912773f7db93ee",
        "nl": false,
        "rap": true,
        "rh": 0,
        "inputs": 0,
        "x": 170,
        "y": 420,
                "191edada74781373",
                "d3347086d32027ca",
                "d321e94ddc708b4a",
                "5624399ecc1ccfc9"
        "id": "191edada74781373",
        "type": "change",
        "name": "payload.DS18B20.Temperature",
        "rules": [
                "t": "set",
                "p": "temp_amb",
                "pt": "flow",
                "to": "payload.DS18B20.Temperature",
                "tot": "msg"
                "t": "set",
                "p": "temp_amb",
                "pt": "msg",
                "to": "temp_amb",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 530,
        "y": 420,
                "da16bc54c2ef5db2"
        "id": "ae60fe1eeac4218f",
        "type": "mqtt out",
        "topic": "cmnd/thermostat/ot_tboiler",
        "qos": "1",
        "retain": "",
        "respTopic": "",
        "contentType": "",
        "userProps": "",
        "correl": "",
        "expiry": "",
        "x": 400,
        "y": 100,
        "id": "8af3775d92279529",
        "type": "inject",
        "props": [
                "p": "payload"
                "p": "topic",
                "vt": "str"
        "repeat": "3600",
        "crontab": "",
        "once": true,
        "onceDelay": 0.1,
        "topic": "",
        "payload": "60",
        "payloadType": "num",
        "x": 150,
        "y": 100,
                "ae60fe1eeac4218f"
        "id": "d3347086d32027ca",
        "type": "switch",
        "name": "OPENTHERM",
        "property": "payload.OPENTHERM",
        "rules": [
                "t": "hask",
                "v": "conn",
                "vt": "str"
        "checkall": "true",
        "repair": false,
        "outputs": 1,
        "x": 460,
        "y": 480,
                "9925554e77622b21"
        "id": "9925554e77622b21",
        "type": "function",
        "name": "OT MESSAGE",
        "func": "msg.ot_status1 = msg.payload.OPENTHERM.conn +\n    \"&nbsp&nbsp&nbsp&nbspFLM:\" + msg.payload.OPENTHERM.FLM +\n    \"&nbsp&nbsp&nbsp&nbspTB:\" + msg.payload.OPENTHERM.TB + \n    \"&nbsp&nbsp&nbsp&nbspTW:\" + msg.payload.OPENTHERM.TDHW + \n    \"&nbsp&nbsp&nbsp&nbspCH:\" + msg.payload.OPENTHERM.SLAVE.CH + \n    \"&nbsp&nbsp&nbsp&nbspFL:\" + msg.payload.OPENTHERM.SLAVE.FL;\n    \nmsg.ot_status2 = \"TBS:\" + msg.payload.OPENTHERM.BTMP.REQ +\n    \"&nbsp&nbsp&nbsp&nbspTWS:\" + msg.payload.OPENTHERM.HWTMP.REQ + \n    \"&nbsp&nbsp&nbsp&nbspWP:\" + msg.payload.OPENTHERM.OT18 +\n    \"&nbsp&nbsp&nbsp&nbspFAULT:\" + msg.payload.OPENTHERM.SLAVE.FAULT;\n    \nreturn msg;",
        "outputs": 1,
        "noerr": 0,
        "initialize": "",
        "finalize": "",
        "libs": [],
        "x": 660,
        "y": 480,
                "da16bc54c2ef5db2"
        "id": "60021c373e8cdb53",
        "type": "change",
        "name": "ot_status",
        "rules": [
                "t": "set",
                "p": "ot_status1",
                "pt": "flow",
                "to": "**********************************************",
                "tot": "str"
                "t": "set",
                "p": "ot_status1",
                "pt": "msg",
                "to": "ot_status1",
                "tot": "flow"
                "t": "set",
                "p": "ot_status2",
                "pt": "flow",
                "tot": "str"
                "t": "set",
                "p": "ot_status2",
                "pt": "msg",
                "to": "ot_status2",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 360,
        "y": 340,
                "bf555a791259f82e"
        "id": "9733bb3381da8ff6",
        "type": "mqtt out",
        "topic": "cmnd/thermostat/ot_ch",
        "qos": "1",
        "retain": "",
        "respTopic": "",
        "contentType": "",
        "userProps": "",
        "correl": "",
        "expiry": "",
        "x": 1170,
        "y": 440,
        "id": "bf555a791259f82e",
        "type": "change",
        "name": "flame_status",
        "rules": [
                "t": "set",
                "p": "flame_status",
                "pt": "flow",
                "to": "false",
                "tot": "bool"
                "t": "set",
                "pt": "msg",
                "to": "flame_status",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 510,
        "y": 340,
                "7a139d8a4e8c1df7"
        "id": "d321e94ddc708b4a",
        "type": "switch",
        "name": "OPENTHERM CH",
        "property": "payload.OPENTHERM.SLAVE",
        "rules": [
                "t": "hask",
                "v": "CH",
                "vt": "str"
        "checkall": "true",
        "repair": false,
        "outputs": 1,
        "x": 470,
        "y": 520,
                "8bddba416ec36bef"
        "id": "8bddba416ec36bef",
        "type": "change",
        "name": "CH STATUS",
        "rules": [
                "t": "set",
                "p": "ch_status",
                "pt": "msg",
                "to": "payload.OPENTHERM.SLAVE.CH",
                "tot": "msg"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 670,
        "y": 520,
                "da16bc54c2ef5db2"
        "id": "5624399ecc1ccfc9",
        "type": "switch",
        "name": "OPENTHERM FL",
        "rules": [
                "t": "hask",
                "v": "FL",
                "vt": "str"
        "checkall": "true",
        "repair": false,
        "outputs": 1,
        "x": 470,
        "y": 560,
                "30909829b5045b31"
        "id": "30909829b5045b31",
        "type": "change",
        "name": "FL STATUS",
        "rules": [
                "t": "set",
                "pt": "msg",
                "to": "payload.OPENTHERM.SLAVE.FL",
                "tot": "msg"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 670,
        "y": 560,
                "da16bc54c2ef5db2"
        "id": "e577dd9a20a8218f",
        "type": "mqtt out",
        "topic": "cmnd/thermostat/ot_twater",
        "qos": "1",
        "retain": "",
        "respTopic": "",
        "contentType": "",
        "userProps": "",
        "correl": "",
        "expiry": "",
        "x": 400,
        "y": 60,
        "id": "5fa6a6aae36ea2b0",
        "type": "inject",
        "props": [
                "p": "payload"
                "p": "topic",
                "vt": "str"
        "repeat": "3600",
        "crontab": "",
        "once": true,
        "onceDelay": 0.1,
        "topic": "",
        "payload": "36",
        "x": 150,
        "y": 60,
                "e577dd9a20a8218f"
        "id": "7a139d8a4e8c1df7",
        "type": "change",
        "name": "ch_status",
        "rules": [
                "t": "set",
                "p": "ch_status",
                "pt": "flow",
                "to": "false",
                "tot": "bool"
                "t": "set",
                "p": "ch_status",
                "pt": "msg",
                "to": "ch_status",
                "tot": "flow"
        "action": "",
        "property": "",
        "from": "",
        "to": "",
        "reg": false,
        "x": 680,
        "y": 340,
                "da16bc54c2ef5db2"
        "id": "f5aafa28f45bf19d",
        "type": "mqtt out",
        "topic": "cmnd/thermostat/Restart",
        "qos": "",
        "retain": "",
        "respTopic": "",
        "contentType": "",
        "userProps": "",
        "correl": "",
        "expiry": "",
        "x": 390,
        "y": 160,
        "id": "7204c37b7a3eaae0",
        "type": "inject",
        "name": "05:00",
        "props": [
                "p": "payload"
                "p": "topic",
                "vt": "str"
        "repeat": "",
        "crontab": "00 05 * * *",
        "once": false,
        "onceDelay": 0.1,
        "topic": "",
        "payload": "1",
        "x": 150,
        "y": 160,
                "f5aafa28f45bf19d"
        "id": "fd52ae383a8b0694",
        "type": "inject",
        "props": [
                "p": "payload"
                "p": "topic",
                "vt": "str"
        "repeat": "3600",
        "crontab": "",
        "once": true,
        "onceDelay": 0.1,
        "topic": "",
        "payload": "10",
        "x": 150,
        "y": 220,
                "6cfe3bed14aba2f3"
        "id": "6cfe3bed14aba2f3",
        "type": "mqtt out",
        "topic": "cmnd/thermostat/TelePeriod",
        "qos": "",
        "retain": "",
        "respTopic": "",
        "contentType": "",
        "userProps": "",
        "correl": "",
        "expiry": "",
        "x": 380,
        "y": 220,
        "id": "e15b980fd008f6a8",
        "type": "ui_group",
        "name": "Termostato Borghi",
        "tab": "d9d243d87692d13f",
        "order": 10,
        "disp": true,
        "width": "6",
        "collapse": false,
        "className": ""
        "id": "51912773f7db93ee",
        "type": "mqtt-broker",
        "name": "Dummy MQTT",
        "broker": "0.0.0.0",
        "port": "1883",
        "clientid": "",
        "autoConnect": true,
        "usetls": false,
        "protocolVersion": "4",
        "keepalive": "60",
        "cleansession": true,
        "birthTopic": "",
        "birthQos": "0",
        "birthPayload": "",
        "birthMsg": {},
        "closeTopic": "",
        "closeQos": "0",
        "closePayload": "",
        "closeMsg": {},
        "willTopic": "",
        "willQos": "0",
        "willPayload": "",
        "willMsg": {},
        "userProps": "",
        "sessionExpiry": ""
        "id": "d9d243d87692d13f",
        "type": "ui_tab",
        "name": "Dashboard",
        "icon": "dashboard",
        "order": 1,
        "disabled": false,
        "hidden": false
Absolutely outstanding, thanks
In case you didn't think about it I would set limits on how high or low you can set the temp. I use 10 as a low limit and 25 as a high limit. This is a personal just because for me.
You're absolutely right.
You'd need to be rich to afford that in the UK right now. :frowning: My max is 20!