Hi, I use your "node-red-contrib-modbustcp".
I want to read 2 spaces of my modbustcp pv converter
I want to get the register 5002 to 5036 and it works well.
But I can not read the registers 12999 to 13077 at the same time 
If I try to read 5002 to 13077 it look like the Array is to big. So I think i have to read it in 2 blocks.
In the doc I read I can use:
[
{
"name": "Reg1",
"address": 4999,
"quantity": 72,
"dataType": "FC4",
"intervall": 15000,
"ieeeBE": true,
"ieeeType": "off"
},
{
"name": "Reg2",
"address": 12999,
"quantity": 78,
"dataType": "FC4",
"intervall": 15000,
"ieeeBE": true,
"ieeeType": "off"
}
]
but it doesn't work.
Please can you help me?
It is not possible to read more than 125 items in a modbus request due to the specification design. You will have to read these in two separate goes. I would recommend you do not poll at the same time but sequence them one after another.
Thanks for answer.
but how I have to do this?
Hi,
I use this ModBus Node https://flows.nodered.org/node/node-red-contrib-modbustcp
If I use there a 2. instance of the node the communication get fail.
The documentation say, I have to use a "multiple input"
[
{
"name": "Reg1",
"address": 4999,
"quantity": 72,
"dataType": "FC4",
"intervall": 15000,
"ieeeBE": true,
"ieeeType": "off"
},
{
"name": "Reg2",
"address": 12999,
"quantity": 78,
"dataType": "FC4",
"intervall": 15000,
"ieeeBE": true,
"ieeeType": "off"
}
]
But if I connect a inject node to the Modbus node I get a thousand messages per second.
I am a newbie in node red.
Can someone please explain to me how I pass the "multiple input" correctly to the Modbus node?
It looks like I am not allowed to upload attachments yet. That's why I save my flow here: